You can learn more about what kind of cookies we use, why, and how from our Privacy policy. If you hate cookies, or are just on a diet, you can disable them altogether too. Just note that the Freshdesk service is pretty big on some cookies (we love the choco-chip ones), and some portions of Freshdesk may not work properly if you disable cookies.
We’ll also assume you agree to the way we use cookies and are ok with it as described in our Privacy policy, unless you choose to disable them altogether through your browser.
Dear Sirs,
got a UG56 that correctly receive status update and send trough mqtt.
This is what I've tried so far:
mosquitto_pub -h broker -t "ug/downlink" -m '{ "devEui":"devicetoOPEN", "confirmed":true, "fPort":85, "data":"ff1d2000" }' mosquitto_pub -h broker -t "ug/downlink" -m '{ "devEui":"devicetoCLOSE", "confirmed":true, "fPort":85, "data":"ff1d0001" }'can see on another subscription terminal
ug/downlink { "devEui":"device", "confirmed":true, "fPort":85, "data":"ff1d2000" }but in network server nothing seems to be received
Instead if I send data to device directly from that page a greyed out row is added .
But no message is published on mqtt when data is sent from th web page ug/uplinkdata. I receive:
{"applicationID":1,"battery":100,"devEUI":"device","deviceName":"YV01","gatewayTime":"2026-05-16T11:09:10+02:00","gpio_1":1,"gpio_2":1,"valve_1":1,"valve_2":0}I need to trigger also commands:
- disable/enable time schedule
- direct command
- change time schedule
Actually device are programmed via NFC.
Can you please tell me how to do it correclty?
Thanks, BR
0 Votes
7 Comments
Chiara posted 7 days ago
Dear Aslan,
thank you for your reply, no worries about the delayed response.
I have now upgraded the UC511 to firmware version 1.7. After repeating Test 1, I can confirm that it completed successfully.
I hope the test script I developed during the troubleshooting process may also be useful for helping other users or for future testing.
I prefer using the built-in timer on the UC511 rather than sending separate Open and Close commands, as I believe it is a safer and more reliable approach for irrigation control.
Thank you for your support, have a nice day!
Best regards
0 Votes
Aslan Lu posted 11 days ago Admin
Hi Chiara,
Thanks for your reply.
Sorry for this late response.
Could you please check and share with us the firmware version and hardware version of your UC511?
We have tested on the latest firmware seems work with the first test.
If you're not using the latest firmware, could you please upgrade it to the latest to test again?
Here's the download link.
https://www.milesight.com/support/resources/firmware
Wish you have a nice day.
0 Votes
Chiara posted 13 days ago
Dear Sirs,
I created a small reproducible test setup for Milesight irrigation valve behavior:
https://github.com/sfoglia/iot_tester/tree/main
If anyone has the same device, I would really appreciate if you could run the script and confirm whether the same behavior occurs.
==============================================================================
TEST 1
Description:
Send only a timed irrigation command.
Expected:
Valve opens immediately and closes automatically after 5 minutes.
==============================================================================
==============================================================================
Timestamp : 2026-07-05 10:47:27
Device : ***************
Command : OPEN valve 1 for 5 minutes
HEX : ff1da0022c0100
Base64 : /x2gAiwBAA==
Topic : ug/downlinkdata
MQTT Payload
{
"devEui":"***************",
"confirmed":true,
"fPort":85,
"data":"/x2gAiwBAA=="
}
==============================================================================
Result : MQTT message published successfully.
wait for timed execution to complete
Observation:
MQTT publish succeeds
No valve actuation observed
TEST 2
Description:
OPEN
wait 60 seconds
CLOSE
wait 5 seconds
OPEN (timed irrigation)
Expected:
Timed irrigation command should execute reliably
==============================================================================
TEST 2
Description:
OPEN
wait 60 seconds
CLOSE
wait 5 seconds
OPEN for 5 minutes
==============================================================================
==============================================================================
Timestamp : 2026-07-05 10:52:33
Device : ***************
Command : OPEN
HEX : ff1d2000
Base64 : /x0gAA==
Topic : ug/downlinkdata
MQTT Payload
{
"devEui":"***************",
"confirmed":true,
"fPort":85,
"data":"/x0gAA=="
}
==============================================================================
Result : MQTT message published successfully.
==============================================================================
Timestamp : 2026-07-05 10:53:33
Device : ***************
Command : CLOSE
HEX : ff1d0001
Base64 : /x0AAQ==
Topic : ug/downlinkdata
MQTT Payload
{
"devEui":"***************",
"confirmed":true,
"fPort":85,
"data":"/x0AAQ=="
}
==============================================================================
Result : MQTT message published successfully.
==============================================================================
Timestamp : 2026-07-05 10:53:38
Device : ***************
Command : OPEN valve 1 for 5 minutes
HEX : ff1da0022c0100
Base64 : /x2gAiwBAA==
Topic : ug/downlinkdata
MQTT Payload
{
"devEui":"***************",
"confirmed":true,
"fPort":85,
"data":"/x2gAiwBAA=="
}
==============================================================================
Result : MQTT message published successfully.
Observation:
OPEN works
CLOSE works
Timed irrigation command is accepted at MQTT level
Additional note (uplink / ack flow)
Observed device behavior after Test 2:
ug/downlinkdata → timed command accepted
ug/uplinkdata → valve task sequence_id changes over time
ug/acknotification → fCnt increments normally
Device telemetry shows alternating task states:
sequence_id: 2 → timed irrigation task present
sequence_id: 0/1 → intermediate/reset states
valve_status: 1/0 → switching states observed
However, final expected stable timed execution is not consistently triggered when the command is issued immediately after OPEN/CLOSE sequence.
Question
Is this:
expected firmware behavior?
a required internal state-machine constraint (cooldown / idle state)?
or a possible firmware issue affecting timed irrigation commands?
Any reproduction feedback from other users would be highly appreciated.
Thanks, BR
0 Votes
Chiara Tecnoelettrica posted about 2 months ago
Dear Aslan,
thank you for information, during testing, I observed that reliable operation requires a minimum activation time after issuing an open command before subsequent actions can be executed.
If the delay is shorter, the valve state does not consistently stabilize, leading to incomplete or missed actuation cycles.
To ensure correct operation, my current sequence is structured as follows:
send open command
wait approximately 60 seconds
send close command
send timed irrigation cycle (now it is executed, if I send only this command is ignored)
Could you please clarify:
What is the recommended minimum stabilization time after an open command?
Is there a preferred command sequence to ensure deterministic valve state (open/close acknowledgment)?
Device are in Class C mode realtime.
I'd prefer to send timed commands as OPEN_V1_5_MIN instead a sequence of open close, but need to understand the expected behavior would help ensure a robust integration.
Best regards
0 Votes
Aslan Lu posted about 2 months ago Admin
Hi,
Thanks for your reply.
Yes, the rain control could suspend scheduled task for a specified period.
Wish you have a nice day.
0 Votes
Chiara Tecnoelettrica posted about 2 months ago
Thank you for the information, you were right: now it works correctly after converting the payload to Base64.
I am currently using:
hex2b64 () { echo -n "$1" | xxd -r -p | base64 } hex2b64 ff1d2000Now I'm playing with opening with timer:
Byte Meaning
ff command group
1d valve task
a0 / a1 flags + valve index
02 sequence_id
xx xx xx duration LE 24 bit
So far I've made python script with tested:
COMMAND_MAP = {
"OPEN": "/x0gAA==", # HEX: ff1d2000
"CLOSE": "/x0AAQ==", # HEX: ff1d0001
"OPEN_V1_2_MIN": "/x2gAngAAA==", # HEX: ff1da002780000
"OPEN_V1_5_MIN": "/x2gAiwBAA==" # HEX: ff1da0022c0100
}
I'd like to add rainy days management but need to understand better what it does: this command would suspend scheduled task for a specified period?
P.S. these devices are truly well designed!
0 Votes
Aslan Lu posted about 2 months ago Admin
Hi,
Thanks for reaching out to us.
The reason Downlink have been failed is the data you send is hex.
Our gateway's MQTT Downlink's data format should be base64.
Please refer to this article to send Downlink command via MQTT.
https://support.milesight-iot.com/support/solutions/articles/73000514114-how-to-remotely-control-devices-via-mqtt-on-milesight-gateway
Also, here's the MQTT API document in case you want control or other feature of our gateway.
https://resource.milesight.com/milesight/iot/document/ug-mqtt-api-documentation-en.pdf
Last, the command to configure UC511, you could refer to User guide, in the last session Chapter 6. Uplink Packets and Downlink Commands.
https://resource.milesight.com/milesight/iot/document/uc51x-series-user-guide-en.pdf
You could find the command you want and use other tools to change it to base64, then send it via MQTT to control the sensor.
Wish you have a nice day.
Best regards,
Aslan